![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/09/2014 12:23 PM EST
|
Chad D
Batman
![[Avatar]](/images/avatar/76dc611d6ebaafc66cc0879c71b5db5c.jpg)
Joined: 06/24/2014 08:55 AM EDT
Messages: 782
Location: Marquette Heights (Peoria) IL
Offline
|
During a recent inspection, I found a small section (about 2 ft) of CSST that connected the gas line to the furnace. Is there a length requirement for bonding CSST? Or is it just safer to have all CSST bonded?
|
Chad Dunham
Eagle's Nest Inspections
Home Inspections
203K Consulting
Indoor Air Quality (IAQ) Testing
Radon Testing
Mold Testing
309-323-0252
http://www.peoriailhomeinspections.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/09/2014 02:15 PM EST
|
Cameron Anderson
P. Diddy
![[Avatar]](/images/avatar/f85454e8279be180185cac7d243c5eb3.jpg)
Joined: 09/27/2014 09:37 AM EDT
Messages: 602
Location: Peoria, IL
Offline
|
All manufacturers that I know of require bonding and have for several years. Some municipalities around here even have upgrade programs which require it if CSST is found in a home.
Are you certain it was CSST and not an appliance connector?
This message was edited 1 time. Last update was at 11/09/2014 02:16 PM EST
|
Cameron Anderson
Illinois Licensed Inspector
homeinspectionpeoria.com
Inspecting since 2004
309-712-1556
Peoria, Illinois |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/09/2014 05:16 PM EST
|
Juan Jimenez
Seal Team 6
![[Avatar]](/images/avatar/1679091c5a880faf6fb5e6087eb1b2dc.png)
Joined: 06/18/2014 08:53 PM EDT
Messages: 987
Location: Richmond, VA
Offline
|
Chad
It sounds like it was an appliance connector. It can be really confusing to discern between the two. Appliance connectors are yellow, but CSST usually has a yellow or black jacket.
|
http://www.ahouseonarock.com
http://www.chimneysweeprichmond.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/09/2014 06:01 PM EST
|
Keven
RockStar!
![[Avatar]](/images/avatar/fc490ca45c00b1249bbe3554a4fdf6fb.jpg)
Joined: 06/19/2014 02:09 PM EDT
Messages: 111
Location: 28078
Offline
|
Chad I would have to agree with Juan. It most likely was a appliance connector and not csst. Did the yellow flex pipe have a name or brand stamped on it. Do you happen to have a picture.
|
Castle Home & Commercial Building Inspections
www.CastleHomeInspectors.com
https://www.facebook.com/Home.Inspector.NC
704-875-3200
Serving
Charlotte, NC
Mooresville, NC
Hickory, NC
Fort Mill, SC
Myrtle Beach, SC
|
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/09/2014 07:50 PM EST
|
Chad D
Batman
![[Avatar]](/images/avatar/76dc611d6ebaafc66cc0879c71b5db5c.jpg)
Joined: 06/24/2014 08:55 AM EDT
Messages: 782
Location: Marquette Heights (Peoria) IL
Offline
|
It looks like CSST to me. As the yellow jacket by the Black Iron Pipe is peeled back more than it should be.
|
Filename |
IMG_4283.jpg |
Download
|
Description |
|
Filesize |
1320 Kbytes
|
Downloaded: |
1451 time(s) |
|
Chad Dunham
Eagle's Nest Inspections
Home Inspections
203K Consulting
Indoor Air Quality (IAQ) Testing
Radon Testing
Mold Testing
309-323-0252
http://www.peoriailhomeinspections.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/09/2014 07:55 PM EST
|
Juan Jimenez
Seal Team 6
![[Avatar]](/images/avatar/1679091c5a880faf6fb5e6087eb1b2dc.png)
Joined: 06/18/2014 08:53 PM EDT
Messages: 987
Location: Richmond, VA
Offline
|
Well that does look like CSST. I always take note of the brand and type and look up the instructions if I have a question. They are all different. Some companies have a premium type that had different installation instructions. As Cam said, they all typically require bonding.
This message was edited 1 time. Last update was at 11/09/2014 07:56 PM EST
|
http://www.ahouseonarock.com
http://www.chimneysweeprichmond.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/09/2014 07:56 PM EST
|
Chad D
Batman
![[Avatar]](/images/avatar/76dc611d6ebaafc66cc0879c71b5db5c.jpg)
Joined: 06/24/2014 08:55 AM EDT
Messages: 782
Location: Marquette Heights (Peoria) IL
Offline
|
Juan Jimenez wrote:Well that does look like CSST. I always take note of the brand and type and look up the instructions if I have a question. They are all different. Some companies have a premium type that had different installation instructions.
I'll try to keep that in mind for the next time I run into CSST.
|
Chad Dunham
Eagle's Nest Inspections
Home Inspections
203K Consulting
Indoor Air Quality (IAQ) Testing
Radon Testing
Mold Testing
309-323-0252
http://www.peoriailhomeinspections.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/09/2014 08:05 PM EST
|
SheehanThomson
Jedi
![[Avatar]](/images/avatar/d67d8ab4f4c10bf22aa353e27879133c.png)
Joined: 06/18/2014 11:28 PM EDT
Messages: 1715
Offline
|
I thought it was supposed to be black iron once it enters the furnace?
|
www.UtahHomeInspectionHQ.com
www.ChooseOnSite.com
www.UtahHomeInspectionPro.com
www.GoUtahHomeInspection.com
Utah Home Inspection Company providing inspections in Provo, Orem, Springville, Pleasant Grove, Lehi, Eagle Mountain, Sandy, West Valley City, Salt Lake City, & More!
Your Utah Home Inspector,
Sheehan D. Thomson
www.HomeInspectorPro.com
(Best Reporting Software Out There!) |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/09/2014 08:28 PM EST
|
Keven
RockStar!
![[Avatar]](/images/avatar/fc490ca45c00b1249bbe3554a4fdf6fb.jpg)
Joined: 06/19/2014 02:09 PM EDT
Messages: 111
Location: 28078
Offline
|
WOW !
Looks like somebody made up their own short csst flex connector. According to the Gas-Tite manufacturers rep that talked with our association if there is any csst the system should be bonded.
|
Castle Home & Commercial Building Inspections
www.CastleHomeInspectors.com
https://www.facebook.com/Home.Inspector.NC
704-875-3200
Serving
Charlotte, NC
Mooresville, NC
Hickory, NC
Fort Mill, SC
Myrtle Beach, SC
|
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/09/2014 08:32 PM EST
|
Chad D
Batman
![[Avatar]](/images/avatar/76dc611d6ebaafc66cc0879c71b5db5c.jpg)
Joined: 06/24/2014 08:55 AM EDT
Messages: 782
Location: Marquette Heights (Peoria) IL
Offline
|
Keven wrote:WOW !
Looks like somebody made up their own short csst flex connector. According to the Gas-Tite manufacturers rep that talked with our association if there is any csst the system should be bonded.
I went ahead and wrote it up as needing to be bonded.
|
Chad Dunham
Eagle's Nest Inspections
Home Inspections
203K Consulting
Indoor Air Quality (IAQ) Testing
Radon Testing
Mold Testing
309-323-0252
http://www.peoriailhomeinspections.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/09/2014 08:37 PM EST
|
SheehanThomson
Jedi
![[Avatar]](/images/avatar/d67d8ab4f4c10bf22aa353e27879133c.png)
Joined: 06/18/2014 11:28 PM EDT
Messages: 1715
Offline
|
I don't think I've ever seen a bonded CSST line here
|
www.UtahHomeInspectionHQ.com
www.ChooseOnSite.com
www.UtahHomeInspectionPro.com
www.GoUtahHomeInspection.com
Utah Home Inspection Company providing inspections in Provo, Orem, Springville, Pleasant Grove, Lehi, Eagle Mountain, Sandy, West Valley City, Salt Lake City, & More!
Your Utah Home Inspector,
Sheehan D. Thomson
www.HomeInspectorPro.com
(Best Reporting Software Out There!) |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/18/2014 01:52 PM EST
|
Kevin Moore
Bon Jovi
![[Avatar]](/images/avatar/8f14e45fceea167a5a36dedd4bea2543.png)
Joined: 06/18/2014 08:58 PM EDT
Messages: 643
Location: Buffalo NY
Offline
|
I had to take a course just to buy gastite, now i see it on the shelves of home depot
|
Kevin Moore
HomeChex
Radonpro Inc
www.buffalo-home-inspector.com
www.radonaid.com
(716)418-0694 |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/18/2014 05:50 PM EST
|
Mike Casey
General
![[Avatar]](/images/avatar/1c9ac0159c94d8d0cbedc973445af2da.jpg)
Joined: 06/28/2014 07:21 PM EDT
Messages: 1245
Location: San Diego CA
Offline
|
That sure looks like Parker CSST to me. It is okay to direct connect CSST to a non-movable appliance. Some manufacturers (not Parker) indicate their yellow CSST should not be in contact with the metal enclosure at any appliance with a metal vent that protrudes through the roof. It is unusual to see a short made-up connector like that with a steel pipe system. If movable appliance, like a clothes dryer, an approved flexible connector would be required.
Here's a good website for the layperson regarding yellow CSST bonding http://csstsafety.com
I've seen the CSST at the box stores, you still have to take the short written exam there from my understanding to purchase the materials. Not sure that is enforced....
The black jacketed CSST is different. Some don't require the #6 copper bond, they approve the usual #10 bond or the equipment grounding conductor in the appliance (if fed by a branch circuit) as the bond like hard steel.
It gets complicated unfortunately and I see many jurisdictions interpreting the requirements differently.
|
Mike Casey
Director of Education
Home Inspection University
www.HomeInspectionUniversity.com
www.MichaelCasey.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/18/2014 07:05 PM EST
|
Cameron Anderson
P. Diddy
![[Avatar]](/images/avatar/f85454e8279be180185cac7d243c5eb3.jpg)
Joined: 09/27/2014 09:37 AM EDT
Messages: 602
Location: Peoria, IL
Offline
|
Chad D wrote:
I went ahead and wrote it up as needing to be bonded.
That's the right call.
|
Cameron Anderson
Illinois Licensed Inspector
homeinspectionpeoria.com
Inspecting since 2004
309-712-1556
Peoria, Illinois |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/18/2014 09:10 PM EST
|
Kevin Moore
Bon Jovi
![[Avatar]](/images/avatar/8f14e45fceea167a5a36dedd4bea2543.png)
Joined: 06/18/2014 08:58 PM EDT
Messages: 643
Location: Buffalo NY
Offline
|
Mike Casey wrote:That sure looks like Parker CSST to me. It is okay to direct connect CSST to a non-movable appliance. Some manufacturers (not Parker) indicate their yellow CSST should not be in contact with the metal enclosure at any appliance with a metal vent that protrudes through the roof. It is unusual to see a short made-up connector like that with a steel pipe system. If movable appliance, like a clothes dryer, an approved flexible connector would be required.
Here's a good website for the layperson regarding yellow CSST bonding http://csstsafety.com
I've seen the CSST at the box stores, you still have to take the short written exam there from my understanding to purchase the materials. Not sure that is enforced....
Really, you have to take an exam at HD? I'm there all the time never seen anything on it.
|
Kevin Moore
HomeChex
Radonpro Inc
www.buffalo-home-inspector.com
www.radonaid.com
(716)418-0694 |
|
 |
|