Nathan brought this up on a FB post last night. It doesn't get too cold here in Atlanta but I have still tested air conditioners down as low as 19 degrees.
I'm not sure why the fear of testing below a certain temperature is so widespread and why the fear is spreading faster than the education on how to properly test.
For those that wont test, Why? post your reasons here, I'm curious what you tell your clients and agents. and please don't use the "it's in my standards excuse" most of the standards are a joke anyway(another topic). If you do test the AC don't give out the process just yet...
|
"Your Friend in the Inspection Business"
Pete's Friendly Home Inspection
Peter Rossetti
General manager
(67 329-7198 |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 09:28 AM EST
|
SheehanThomson
Jedi
![[Avatar]](/images/avatar/d67d8ab4f4c10bf22aa353e27879133c.png)
Joined: 06/18/2014 11:28 PM EDT
Messages: 1715
Offline
|
I'd like to know the process others use.
|
www.UtahHomeInspectionHQ.com
www.ChooseOnSite.com
www.UtahHomeInspectionPro.com
www.GoUtahHomeInspection.com
Utah Home Inspection Company providing inspections in Provo, Orem, Springville, Pleasant Grove, Lehi, Eagle Mountain, Sandy, West Valley City, Salt Lake City, & More!
Your Utah Home Inspector,
Sheehan D. Thomson
www.HomeInspectorPro.com
(Best Reporting Software Out There!) |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 11:21 AM EST
|
Brad Brinke
Wizard
![[Avatar]](/images/avatar/c20ad4d76fe97759aa27a0c99bff6710.jpg)
Joined: 06/18/2014 09:12 PM EDT
Messages: 156
Offline
|
I disagree Peter, assuming you are talking about AC and not the heat pump. There is oil that is used to lubricate the parts inside the air conditioner and when it gets cold that oil gets sluggish. Newer AC units have sensors that prevent cold weather operation. I would say that testing AC in the winter IS poor service to your clients and the homeowner. What do you hope to gain by seeing if a machine operates well outside of its normal temps? Is the same AC that "works" in January going to work under extreme conditions in August?
|
Inspecting all of Hampton Roads. Over 17 years of experience. Trusted.
www.procraftinspections.com
757.362.2300 |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 12:34 PM EST
|
Peter Rossetti
Certified Pro
![[Avatar]](/images/avatar/9778d5d219c5080b9a6a17bef029331c.jpg)
Joined: 06/21/2014 07:31 AM EDT
Messages: 44
Location: Peachtree City, Georgia
Offline
|
BBrinke, what is normal? Is it really outside normal operating temperatures?
Case in point. Thanksgiving day. double oven is on, all the burners on the stove are going. house is packed to capacity with so many people the fire marshal would cry. kids are running around and the thermostat reads 78 and is fast approaching 80 and beyond. its lets say 35 degrees outside. Do you say no to your guests when they say turn on the air? I don't, I just turn on the air.
|
"Your Friend in the Inspection Business"
Pete's Friendly Home Inspection
Peter Rossetti
General manager
(67 329-7198 |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 12:41 PM EST
|
Kevin Moore
Bon Jovi
![[Avatar]](/images/avatar/8f14e45fceea167a5a36dedd4bea2543.png)
Joined: 06/18/2014 08:58 PM EDT
Messages: 643
Location: Buffalo NY
Offline
|
Peter Rossetti wrote:BBrinke, what is normal? Is it really outside normal operating temperatures?
Case in point. Thanksgiving day. double oven is on, all the burners on the stove are going. house is packed to capacity with so many people the fire marshal would cry. kids are running around and the thermostat reads 78 and is fast approaching 80 and beyond. its lets say 35 degrees outside. Do you say no to your guests when they say turn on the air? I don't, I just turn on the air.
This whole post is outside of normal parameters
|
Kevin Moore
HomeChex
Radonpro Inc
www.buffalo-home-inspector.com
www.radonaid.com
(716)418-0694 |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 01:07 PM EST
|
SheehanThomson
Jedi
![[Avatar]](/images/avatar/d67d8ab4f4c10bf22aa353e27879133c.png)
Joined: 06/18/2014 11:28 PM EDT
Messages: 1715
Offline
|
I would open some windows; that's common sense.
|
www.UtahHomeInspectionHQ.com
www.ChooseOnSite.com
www.UtahHomeInspectionPro.com
www.GoUtahHomeInspection.com
Utah Home Inspection Company providing inspections in Provo, Orem, Springville, Pleasant Grove, Lehi, Eagle Mountain, Sandy, West Valley City, Salt Lake City, & More!
Your Utah Home Inspector,
Sheehan D. Thomson
www.HomeInspectorPro.com
(Best Reporting Software Out There!) |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 01:32 PM EST
|
Peter Rossetti
Certified Pro
![[Avatar]](/images/avatar/9778d5d219c5080b9a6a17bef029331c.jpg)
Joined: 06/21/2014 07:31 AM EDT
Messages: 44
Location: Peachtree City, Georgia
Offline
|
Kevin M, you must not have a huge Italian family that loves the holidays
from what I've seen/read/experienced it is more likely for the evaporator coil to freeze before any damage to the compressor happens in my scenario.
it would be more potentially damaging to the compressor to run the house down to 58 degrees if its 90 degrees outside than it would be to run it during my Thanksgiving scenario.
|
"Your Friend in the Inspection Business"
Pete's Friendly Home Inspection
Peter Rossetti
General manager
(67 329-7198 |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 01:52 PM EST
|
Kevin Moore
Bon Jovi
![[Avatar]](/images/avatar/8f14e45fceea167a5a36dedd4bea2543.png)
Joined: 06/18/2014 08:58 PM EDT
Messages: 643
Location: Buffalo NY
Offline
|
Peter Rossetti wrote:Kevin M, you must not have a huge Italian family that loves the holidays
from what I've seen/read/experienced it is more likely for the evaporator coil to freeze before any damage to the compressor happens in my scenario.
it would be more potentially damaging to the compressor to run the house down to 58 degrees if its 90 degrees outside than it would be to run it during my Thanksgiving scenario.
No I'm Irish
|
Kevin Moore
HomeChex
Radonpro Inc
www.buffalo-home-inspector.com
www.radonaid.com
(716)418-0694 |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 02:56 PM EST
|
Brad Brinke
Wizard
![[Avatar]](/images/avatar/c20ad4d76fe97759aa27a0c99bff6710.jpg)
Joined: 06/18/2014 09:12 PM EDT
Messages: 156
Offline
|
Peter Rossetti wrote:BBrinke, what is normal? Is it really outside normal operating temperatures?
Case in point. Thanksgiving day. double oven is on, all the burners on the stove are going. house is packed to capacity with so many people the fire marshal would cry. kids are running around and the thermostat reads 78 and is fast approaching 80 and beyond. its lets say 35 degrees outside. Do you say no to your guests when they say turn on the air? I don't, I just turn on the air.
I'm Brad btw. Yes, you open windows. How can you tell an AC is properly working when its 35 degrees outside?
|
Inspecting all of Hampton Roads. Over 17 years of experience. Trusted.
www.procraftinspections.com
757.362.2300 |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 04:01 PM EST
|
Peter Rossetti
Certified Pro
![[Avatar]](/images/avatar/9778d5d219c5080b9a6a17bef029331c.jpg)
Joined: 06/21/2014 07:31 AM EDT
Messages: 44
Location: Peachtree City, Georgia
Offline
|
Brad,
Properly working... how should i know when its that cold out. I don't do a full inspection at these temperatures. There is a process I follow that will let me know if the compressor is working.
|
"Your Friend in the Inspection Business"
Pete's Friendly Home Inspection
Peter Rossetti
General manager
(67 329-7198 |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 05:12 PM EST
|
Juan Jimenez
Seal Team 6
![[Avatar]](/images/avatar/1679091c5a880faf6fb5e6087eb1b2dc.png)
Joined: 06/18/2014 08:53 PM EDT
Messages: 987
Location: Richmond, VA
Offline
|
I don't necessarily disagree with you Peter, but this is different than opening water valves or turning on a fire place. If you read an AC manual, they often warn against turning on an AC below a certain temperature. A lot of HVAC technicians say its crap though, but i am not an HVAC technician. For now, I defer to the manuals.
|
http://www.ahouseonarock.com
http://www.chimneysweeprichmond.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 06:45 PM EST
|
mikeauger
Gangster
![[Avatar]](/images/avatar/dc6a6489640ca02b0d42dabeb8e46bb7.jpg)
Joined: 10/21/2014 06:28 PM EDT
Messages: 242
Location: Rhode Island
Offline
|
Peter Rossetti wrote:Nathan brought this up on a FB post last night. It doesn't get too cold here in Atlanta but I have still tested air conditioners down as low as 19 degrees.
I'm not sure why the fear of testing below a certain temperature is so widespread and why the fear is spreading faster than the education on how to properly test.
For those that wont test, Why? post your reasons here, I'm curious what you tell your clients and agents. and please don't use the "it's in my standards excuse" most of the standards are a joke anyway(another topic). If you do test the AC don't give out the process just yet...
in addition to possible damage operating a frozen system...How do you determine the system is cooling effectively, not just the fan spinning? Temperature drop. If the inside air is 68, and the outside temp is 10, the air will show a drop in air temp because the coolant gets cold due to ambient air temp, it could still be broken, non functional, etc...false temp drop, and If you cant rely on the temp drop as accurate because of this, what are you even doing then, you cant give it a "pass" anyway? Just my 2 cents, I don't test it in the cold. Keep in mind it can be much colder in New England than Georgia.
|
Mike Auger, CMI
Patriot Property Inspections
RI Home Inspector
RI Reg. # 32856
RI Radon Lic. # RMC-142 RMB-096
401-578-4878
www.homeinspectorri.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 07:00 PM EST
|
Brad Brinke
Wizard
![[Avatar]](/images/avatar/c20ad4d76fe97759aa27a0c99bff6710.jpg)
Joined: 06/18/2014 09:12 PM EDT
Messages: 156
Offline
|
Peter Rossetti wrote:Brad,
Properly working... how should i know when its that cold out. I don't do a full inspection at these temperatures. There is a process I follow that will let me know if the compressor is working.
Spill the beans then.
This thread is titled "Not testing the AC in winter is poor service to your client". You posted this and then you say you don't care if its properly working.
|
Inspecting all of Hampton Roads. Over 17 years of experience. Trusted.
www.procraftinspections.com
757.362.2300 |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 08:10 PM EST
|
Kevin Moore
Bon Jovi
![[Avatar]](/images/avatar/8f14e45fceea167a5a36dedd4bea2543.png)
Joined: 06/18/2014 08:58 PM EDT
Messages: 643
Location: Buffalo NY
Offline
|
bbrinke wrote:
Peter Rossetti wrote:Brad,
Properly working... how should i know when its that cold out. I don't do a full inspection at these temperatures. There is a process I follow that will let me know if the compressor is working.
Spill the beans then.
This thread is titled "Not testing the AC in winter is poor service to your client". You posted this and then you say you don't care if its properly working.
I personally think that if you cant do an accurate, full inspection of the system you are better off disclaiming it. Lots of times here the agents escrow 2k until it can be properly tested.
|
Kevin Moore
HomeChex
Radonpro Inc
www.buffalo-home-inspector.com
www.radonaid.com
(716)418-0694 |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 12/03/2014 11:00 PM EST
|
Cameron Anderson
P. Diddy
![[Avatar]](/images/avatar/f85454e8279be180185cac7d243c5eb3.jpg)
Joined: 09/27/2014 09:37 AM EDT
Messages: 602
Location: Peoria, IL
Offline
|
bbrinke wrote: I'm Brad btw. Yes, you open windows. How can you tell an AC is properly working when its 35 degrees outside?
No one can, that's what makes this and threads like it so absurd. No one is truly "testing the AC" at these temps. That is an exaggeration and if you advertise it as such to clients you are at best misleading and at worst outright lying. I don't listen to the refrigerator cycle on and then proclaim to my client, "Never fear! Your inspector has officially "tested" the frig! What a super USP I provide!"
Unless the AC is equipped with low ambient controls, you risk damage. Why that fact is so flippantly ignored, I will never understand.
|
|
 |
|